So, you’ve got an electrical appliance to run, but no place to plug it in. When you need to run a regular household electrical type device in an area where no regular grid power is available, this calculator will help you figure out what size batteries and power inverter you need!

Welcome to our DC/AC conversion tool (with inverter). This calculator is designed to assist you with power usage amounts, when converting from one power form to another using a DC to AC inverter.

Just enter power numbers in the fields below, and we will do the calculations for you, including typical inefficiencies and all that other techie type stuff you may not care to calculate. If you are not sure of your numbers, have a look at the walkthrough illustrations below when entering numbers.

If you want to size your inverter battery pack, then you first need to figure out the DC amperage you will be pulling out of your battery pack through the inverter. This calculator can assist you in figuring out the DC amp draw through an Inverter, so you can accurately size your inverter battery pack.

Enter AC Device Ratings
AC Voltage VAC
AC Amperage Amps AC (enter mAh as .xyz)
Wattage 0 Watts
DC Voltage   12 V     24 V     36 V     48 V
DC Amperage 0 Amps DC

Find Your Battery     Choose Your Inverter

Walkthrough

Photo Icon
Example
AC Voltage - Many applications will have a range of Input AC voltage. In the US, it can be anywhere from 100-125 VAC. In Europe, it's usually 200-240. For this example, we'll use the US standard of 120 Volts AC.

Photo Icon
Example
AC Amperage - Input Amperage is how much current the application draws from the AC power. This number is usually rated in Amps. If the current is rated in milliamps (mAh) you can convert it to Amps by dividing the number by 1000. For instance, our example application draws 300 milliamps, which is the same as 0.3 Amps.

Photo Icon
Example
Wattage - Wattage is the total amount of power the application uses. It's calculated by multiplying voltage by amperage. Therefore the 120 VAC x 0.3 Amps equals 36 Watts.

Photo Icon
Example
DC Voltage - Output Voltage is rating of your battery system, usually a single 12 volt battery. We use 12.5 volts for 12 volt battery systems.

Photo Icon
Example
DC Amperage - Now we know that our application uses 36 watts of total power. If you take this power from a 12.5 VDC source, then the total amperage required increases to 3.31 Amps, or 3,310 milliamps. Since batteries have a limited capacity, or amp hours, it's important to size a battery large enough to handle the amperage demand for your application.

Find Your Battery     Choose Your Inverter


Was this information helpful? Sign up to Get Updates and Offers.

Email address should be formatted user@domain.com
We respect your rights to privacy and will not share your email information with anyone ever.
59 people commented, Tech, Emmanuel, Lodge, Chris S., and 55 others
This article is rated 4.6 out of 5
For Questions and Tech Support, please submit your question with our Support Page.

Should contain only letters, numbers, and (' - .)!

   1   2   3   4   5

Subscribe to comments with RSS.

  • Emmanuel I have a 12v car battery and I also have 240v electric motor. So can the 12v battery run the electric motor???

    Reply  •  Ratted article 2  •  June 3, 2020 at 11:10 pm
    • BatteryStuff Tech Unfortunately, no. Depending if the motor is an AC or DC motor you would need either inverter or converter to run the motor off of a battery.

      Reply  •  Ratted article 5  •  June 15, 2020 at 1:46 pm
  • Chris Sims What I am about to ask will most likely make you cringe, but with that said. I have a car audio amplifier and subwoofer set up that i can no longer use in my vehicle. It is a 2000 watt amp when connected to a 1 ohm load. The subs play real low, like down to 25hz. Which makes me want to bring this inside for movies. Stupid idea, I know. However, I am still interested in repurposing this setup. The question I am asking is beyond my comprehension, so please be patient. If the amp pulls around 200 amps DC to create 2000 watts at 1 ohm. How does that equate to AC? The standard breaker in my house is 15 amp's, with a few at 20. Is there a power invertor that can plug into a 120 volt outlet and provide the power needed for the amp? Would it require a 220 volt? Would that still not be enough power? Any help will be appreciated. If you need more information, please let me know.

    Reply  •  Ratted article 5  •  April 28, 2020 at 7:55 am
    • Lodge Ok Chris to support this in a home application you are going to need a large 12 volt power supply, for 2000 Watts you will basically be going with switched mode power supply, now I'm not saying you can't use a transformer based but they will be heavy and expensive, if you want something light, small, go switched mode, the thing to ask Batterystuff is, can there power supplies be parralled, some types will support this and get two, parrallel them and your good to go like the 12 volt 90 amp ones, and it would be even better if they can be adjusted slightly to 13.8 volts, again some supplies will have offer adjustment just ask the seller, and a 240 volt 20 Amp plug will safely run at 80% loading, about 3800 watts and normally it's easy for an licensed sparky to change one of your plugs over without needing to rip up your walls and make a mess in your house to 240-20 amp, it's actually common for larger AC units or bitcoin miners.

      Reply  •  Ratted article 5  •  June 3, 2020 at 12:26 pm
    • Chris S. It’s not entirely stupid, it’ll give you nice sound but depending on your exact setup there may be syncopation effect where the timing is off from the rest of the system, like the site said there may be some trial and error involved, but assuming the 2000w amp is peak draw you may want to search for an inverter with that draw on a single channel. Be warned the cooling fan at that rating is likely to be loud. You could place a car audio capacitor inline between the inverter and the amp just like you would on a vehicle.

      Reply  •  Ratted article 5  •  May 19, 2020 at 1:29 pm
    • BatteryStuff Tech First we are not audio experts, so you may want to talk to an audio tech regarding your setup... In the end if you want to use a 12v stereo with AC power you will need a Power Supply / Converter Charger to power your equipment. Most of these can run off of a 15 amp breaker, with the exception of the 75 amp needing a 20 amp, and the 90 or 100 amp needing a 30 amp breaker. In most setups you would need a deep cycle battery meant to act as a buffer for the larger amp draws the power-supply isn't capable of outputting. Given you are no longer going to have a large amp alternator working as a power-supply you will most likely need an larger battery pack to act as a buffer. I would suggest giving our tech line a call for further information, but a lot of this may be trial an error till you come up with the right system. In the end the music being played can greatly affect your power requirements, so what works for one person may not work for another.

      Reply  •  Ratted article 5  •  April 28, 2020 at 8:26 am
  • Adam Penny Love it. Gives me a better understanding when using AC appS. Inverted From DC solar system

    Reply  •  Ratted article 5  •  March 5, 2020 at 4:33 am
  • Ryan McAteer So, if I have four 6v (200ah) batteries in series and parallel giving me a total of 400ah with a 12v inverter or if I have four 6v (200ah) batteries in series giving me a total of 200ah with a 24v inverter --- i'm not really losing any capacity (ah) because in a 24v battery bank the "appliances" would only pull half of the amps it needs, is this correct? of course both inverters a pure sine.

    Reply  •  Ratted article 5  •  February 19, 2020 at 6:07 am
    • TECH You are correct when it comes to the amp draw a 24v inverter will pull half the amps then a 12v inverter. You are also correct you won't see any loss if you use the same amount of batteries in your 12v setup as you would in the 24v setup. The biggest difference is when your AH remains the same... Take for instance a 12v 200 AH battery bank and a 24v 200 AH battery bank. In this case the you might think the 24v bank would last only double the time, but it actually last a little longer than double. The more amps you pull out of a battery bank the less AH capacity that battery bank is, which is why most batteries have several different AH ratings based off the Amp draw the battery is subjected to. In this case a 12v 200 AH battery pack could withstand a 10 amp draw and last only 10hrs, but the 24v 200 AH battery bank lasts 21hr 41 min. In this scenario you get an additional 1hr 41min of run time due to the less amps being drawn out of the higher voltage battery pack.

      Reply  •  Ratted article 5  •  March 6, 2020 at 10:31 am
  • Randy Edward Marshall I have a small camper that I only use electricity for a few led lights and a small tv with a total load of about 75 watts at 110v I have a small 150w inverter about how long will a 100amp hour battery last before it would need to be recharged? Thanks

    Reply  •  Ratted article 4  •  December 7, 2019 at 4:24 pm
    • BatteryStuff Tech Randy, even though 75 watts doesn't seem like much it can draw the battery down pretty quickly. If you inputted 110VAC at 0.68 Amps your at about 75 watts, which equates to 6.88 DC amps. You can take that figure and input it into our Calculator | Sizing a 12 Volt Battery to a Load. Ideally, you should input the hours you intend to run the inverter for, but i can tell you the 75 Watt load will drain the battery 50% in about 6.5 hrs. At that time you would need to recharge the battery to prevent excess discharge. In most situation like yours we typically see people using a much larger battery pack if they are wanting to run a TV. Obviously, this load only accounted the 75 watts, so with all of the other accessories you could easily be excessively discharging the battery each night depending on how much you are using the TV and other accessories. Most customers that intend to use an inverter and dry camp will typically start with a battery pack in the 200+ AH range.

      Reply  •  Ratted article 5  •  December 13, 2019 at 7:37 am
  • Rick Nicholson This calculator is almost spot on, it would be best if you could choose either to list amps or watts. Remember you're making this calculator for newbies, so yes I know you can divide watts by 120 (north america) and get the amps, but for newbies, easier if you can enter either.

    Reply  •  Ratted article 4  •  February 28, 2019 at 10:54 am
  • Scott Bell I have a electric motor 220amp. it does not show how many watts info on the motor. Is there a way to find out how many 12volt

    Reply  •  Ratted article 5  •  November 28, 2018 at 10:19 am
    • BatteryStuff Tech Volts x Amps = Watts - If your looking for the wattage you can use this calculation. If this is an AC powered device you can input your AC voltage and Amperage into the calculator above to get both your wattage and DC Amps.

      Reply  •  Ratted article 5  •  November 30, 2018 at 8:57 am
  • Larry nice handy calucator for inverters Thanks so much

    Reply  •  July 19, 2016 at 4:11 pm
  • John It is hot in Houston. I have a 2000 Btu air conditioning with a power consumption of 270 watts and a nominal current of 2.9A plus a starting current at 13.9A while attempting to use 12vdc battery. What wattage inverter do I need? And how long do you think a car battery will last using the above setup?

    Reply  •  Ratted article 2  •  July 4, 2016 at 6:38 am
    • BatteryStuff Tech At 120VAC @ 2.9 amps your are drawing approximately 32 Amps a hour out of a battery. You would be lucky if a car battery could take that draw for even an hour before excessively discharging the battery. I would use our Calculator | Sizing a 12 Volt Battery to a Load, and just be sure to put in the DC amp draw of 32 Amps, and not the AC amp draw. As far as what inverter to purchase… You need to account for your surge draw which you state is 13.9 amps… 120VAC x 13.9 Amps = 1,668 Watts! The inverter you select must be able to handle that draw, and you might want to talk to the manufacturer to see how long that surge lasts. Most inverters come with a surge rating for less than a second, so if your surge last longer it generally forces you into a larger inverter.

      Reply  •  January 25, 2017 at 7:50 am
  • Ogboi Stephenson ls I have a DC appliances that’s uses -48v and the current in my region is an AC with 200v – 220v, how do I get an accurate result?

    Reply  •  Ratted article 5  •  July 4, 2016 at 1:59 am
    • BatteryStuff Tech If your device runs off 48 volts then there is no need to be looking for an inverter. Your device is meant to run off either a 48v power-supply, or a 48v battery pack.

      Reply  •  January 25, 2017 at 7:19 am
  • Steve Southen i have a 5000 watt invertor fitted to my nissan patrol ute .
    so how many 12volt batteries would i need to get max 240 volt power out of the invertor ???????

    Reply  •  Ratted article 1  •  June 30, 2016 at 5:01 am
    • BatteryStuff Tech As you can see by the calculator that would draw about 460 Amps an hour out of a 12v battery pack! Next I would suggest using our Calculator | Sizing a 12 Volt Battery to a Load, as it depends on how long you want to run that load for…

      Reply  •  January 19, 2017 at 10:28 am
  • Kais amazing useful

    Reply  •  Ratted article 5  •  May 4, 2016 at 1:50 am
  • Warren This tool was helpful. Just a quick question. I guilt a solar generator with a 100 watt panel, a 12V inverter that puts out 220 VAC and a 12 V battery. It is supposed to run a stock well that is 480 Amps. With just one battery it only runs 3 minutes the overloads the battery. If I read the calculator right this pump will draw 9715.20 Amps DC, but each 12 V battery will only put out 3,310 milliamps. So if I connect 3 12 V batteries in parallel, will that be sufficient to run this pump or should I connect 4 12 V Batteries?

    Reply  •  April 20, 2016 at 9:19 pm
    • BatteryStuff Tech Now that you used this calculator to determine what you will be drawing out of the battery. I would suggest using our Calculator | Sizing a 12 Volt Battery to a Load. This calculator will tell you what size battery pack you need to create depending on how long you want to run the well for.

      Reply  •  Ratted article 5  •  April 21, 2016 at 12:03 pm
  • Jason Can I use this in reverse? I have a 100A 240V sevvice but need to power a DC rectifier shelf that is capable of 200A. If I use this calculator and input 100A AC, 240VAC, 48VDC then the calculator shows 552A DC. DOes this mean that the 100A AC service can supply up to 552A DC?

    Reply  •  October 31, 2014 at 11:53 am
    • BatteryStuff Tech In reverse it would be a charger vs an inverter, however if the charger runs off 240VAC and draws a 100A then it will put out approximately 552A on a 48V system, but it might vary depending on the efficiency of the charger.

      Reply  •  Ratted article 5  •  November 19, 2014 at 10:23 am
  • Ron I have a portable 5000 BTU air conditioner unit. The tag shows that it uses 504 watts and 4.5 to 4.8 Amps. It runs very well with a 1200 watt generator. How long can it run using an inverter, a 100 amp hour AGM battery rated at 1200 watts?

    Reply  •  Ratted article 5  •  September 11, 2014 at 9:19 am
    • TECH 504 watts / 4.8 Amps = 105 VAC. This would pull 46.37 Amps DC, so you could run about an hour before you start to excessively discharge the battery.

      Reply  •  Ratted article 5  •  September 25, 2014 at 10:18 am
  • Fizi Great tool.

    If you add inverter efficency as an optional input that might be good as well.

    Reply  •  Ratted article 5  •  September 6, 2014 at 4:51 am
    • BatteryStuff Tech Glad to help! I will send your recommendation up the food chain and see if we can make it happen!

      Reply  •  September 12, 2014 at 1:07 pm
  • Sambo Thanks, this was very helpful, but mainly to give me an idea of the current draw on the batteries so that I can work out what circuit breaker/fuse to get.

    Reply  •  August 26, 2014 at 4:13 am
  • BatteryStuff Tech Either the multi-meter is hooked up backwards, or you have forced the batteries to charge backwards. Usually you are reading the reverse terminals.

    Reply  •  August 22, 2014 at 9:45 am
  • Najm hi,
    why do we hav some devices taking negative voltage?
    e.g BTS operates in -48V (DC)

    Reply  •  August 21, 2014 at 5:14 am
  • Admin Due to the fact that we don’t have all the information for your system we would need you to contact us at tech@batterystuff.com so that we can ask the appropriate questions, to get you the answer that you may need.

    Reply  •  August 15, 2014 at 2:25 pm
  • Bill Mertz Good morning.
    I have calculated that I need 300 Amps DC per day.
    How many 250 watt 12 volt solar panels do I need to keep up with this demand.
    My battery bank is 3000Ahs 12 volts.
    Regards
    Bill

    Reply  •  August 13, 2014 at 11:30 am
  • Bill Mertz This is GREAT stuff.
    Thank you ALL for the info.

    Reply  •  Ratted article 5  •  August 12, 2014 at 10:07 pm
  • Mike I have a 24VDC power bay with a DC to DC convertor (-48VDC). If I’m reading 30amps on -48VDC side how much power is my 24VDC bay actually providing?

    Reply  •  June 23, 2014 at 2:52 pm
    • BatteryStuff Tech That depends on the efficiency of the converter. On the 48 volt side, you are using essentially 1450 watts. The wattage on the other side, the 24v side, will depend on the efficiency of the conversion process.

      Reply  •  June 25, 2014 at 9:05 am
  • Jonathan Burns Hi tbere i am looking to no how long my 240 appliances will last for with 2 110 batteries working of a 1500watt inverter drawing 980watts in total a total of 88 odd amps of dc how long will my batteries last and what size of solar panel would suit to maintain my batteries as i have only a splitt relay wired as a charging system

    Reply  •  Ratted article 5  •  June 17, 2014 at 9:01 pm
    • BatteryStuff Tech 240VAC doesn’t change the total power of the system. The same calculations will work. In your case, you will get roughly an hour 1/2 of run time.

      Reply  •  June 20, 2014 at 11:55 am
  • John i wish to power a series of appliances whose total sum of wattage is 720 watts for a minimum of 3 hrs non stop. i have already purchased a 12v – 220v inverter which is rated 1500watts…my questions aer: what rating of one 12v battery (or a system of combined batteries) do i need to achieve this target.Also , what specification of solar panel charging system can charge the battery in a very short time like 2 hours of sunlight…we do have intense sunlight in my region.

    thanks

    Reply  •  Ratted article 5  •  May 26, 2014 at 6:41 am
    • Admin Please email your question to tech@batterystuff.com

      Reply  •  May 27, 2014 at 9:45 am
  • Jordan Would this calculator also work if I wanted to know what a switch that was rated AC would handle in DC?

    Reply  •  Ratted article 5  •  June 17, 2013 at 11:36 am
    • BatteryStuff Tech Jordan, this calculator is a simple AC to DC conversion. It will not work for your situation. Thanks

      Reply  •  May 21, 2014 at 12:35 pm
  • Shelly Ok I used your tool above (THANK YOU SO MUCH FOR THIS TOOL) to determine the battery I will require to run my 5V 2A device from a 12volt battery. The tool returned .92amp DC. So my question is how can I now determine what size battery in amp hours I require to run this device for 10 hours?

    Reply  •  April 11, 2013 at 9:05 am
    • Jeremy Fear www.batterystuff.com/kb/tools/calculator-sizing-a-battery-to-a-load.html

      Reply  •  April 12, 2013 at 7:49 am
  • Hector DC to AC amperage conversion run through an Inverter.
    What is the correct explanation of why requires 5 DC amps per each AC amp?

    Reply  •  April 4, 2013 at 7:11 am
    • Jeremy Fear Amperage is the flow of electricity, while voltage is the pressure. Saying that it requires 5amps DC to 1 amp AC is not a correct statement. What is true is that in a 13volt (12 volt nominal) DC system, ran through an inverter that is about 80% efficient, the total power useage is approximently 78 watts, which would be a little under 1 amp at 115VAC. Wattage is the total power, which is comprised of voltage * amperage. If you change the voltage, but leave the wattage (total power) the same, then the amperage has to change as well.

      Reply  •  April 4, 2013 at 9:21 am
  • Gops nice tool thanks for your information .can you explain about %loss calculation

    Reply  •  March 19, 2013 at 3:43 am
    • Jeremy Fear The loss figured is based upon the average efficiency for Pure Sine Wave power inverters. In this case, 15% loss, or 85% efficiency.

      Reply  •  March 19, 2013 at 10:31 am
  • RAJAVARDHANA NAIDU.G span class="caps">VERY NICE TOOL.

    Reply  •  February 27, 2013 at 2:50 am
  • Tim When talking about current, for example if a device is drawing 3 amps, does that mean 3amps per hour?
    So if your drawing 3 amps from a 3amp/hour battery, that battery would last about 1 hour? Right?

    Reply  •  Ratted article 4  •  February 4, 2013 at 12:04 pm
  • Ram Nice tool
    Thanks

    Reply  •  Ratted article 5  •  November 28, 2012 at 8:20 am
  • Thanos Nice tool!
    Thanks
    Good idea to add the % of losses too!

    Reply  •  November 24, 2012 at 4:30 am
  • Zuki This was exactly what I was looking for. I would like to have the formula though just in case I need to do it the old fashioned way.

    Reply  •  October 31, 2012 at 2:47 pm
    • BatteryStuff Tech The calculator uses Ohm‘s Law. Watts = Volts x Amps. We additionally take into consideration an average inefficiency rate of 15% because the power is passing through an inverter. Once you find the watt amount from the AC volts x amps, you can divide the watts by DC volts to get DC amps, plus 15%. Without the efficiency loss, AC or DC watts will always be the same because it is total power. But as voltage goes up or down, in order to have the same power the amps will adjust accordingly.

      Reply  •  October 31, 2012 at 3:09 pm
      • Dave Very useful. But I believe Watts = Volts x Amps is Watts law. Not Ohms law.

        Reply  •  Ratted article 5  •  May 19, 2014 at 2:12 pm
        • BatteryStuff Tech Dave, that is correct. Thanks for the correction. Ohm’s law is V=I*R, Watt’s law is W=V*I, where V=voltage, I= current, R= Resistance, W= Wattage.

          Reply  •  May 21, 2014 at 12:48 pm